Power0020
Electrical
- Jun 11, 2014
- 303
a 230/115 kV interconnection station ,needs to be energized from 230 kV side,
After clearing commissioning steps and tests, I presume the following sequence:
1- the 230 kV bus will be livened first by one incoming feeder with all other breakers open.
2?- the power transformer 230 kV CB is closed.
3- *overriding the interlock* after about 24 hours, 115 kV CB is closed and other CBs accordingly.
This looks very systematic. However, I am worried about energizating a 230 kV transformer from a long OHTL and leaving it unloaded. I had similar experience when investigation system transients with ferroresonace arising from no load current, line capacitance and core non-linearity.
Any clue?