Mbrooke
Electrical
- Nov 12, 2012
- 2,546
We have a situation where two 132 kv lines link between two 400kv-132kv substations feed a dozen 132-33/11kv substations. Under certain contingencies such as the loss of 400kv autotransformers or the loss of 400kv lines linking these two 400-132kv substations, the remaining 132kv lines begin to thermally overload. Generation dispatch change does not resolve the excessive load flow. Currently the problem is mitigated by a protection relay package which trips the 132kv buss tie breakers at the remote 132-33kv substations turning two circuits into 4 radial transmission lines.
The concern is that should a fault occur on any one of these transmission lines during radial operation, up to 85MW of load will be lost and 175MW for the loss of both lines in the same right-of-way. Under normal conditions this loss of load is mitigated via operating all 132kv line protection and buss tie breakers in these 132-33/11kv substations normally closed. During a fault POTT and zone selective deferential relaying only trip the breakers immediately in between the faulted line resulting in no loss of transmission supply to power distribution transformers. Distribution feeders are only exposed to a voltage sag of 6 to 20 cycles during normal clearing time. Running these lines normally closed is very advantageous from a service continuity and reliability goals stand point.
The two options being considered are the insertion of a series reactor in each 132kv line bay or the insertion of a phase angle regulator (PAR) on each line.
The only other option is a theoretical relaying system which closes the opened 132kv breaker during a fault and then opens only the breakers between the fault segment like seen during normally closed operation however I have never heard or even seen of such. (Though I do ask if it exists).
The concern is that should a fault occur on any one of these transmission lines during radial operation, up to 85MW of load will be lost and 175MW for the loss of both lines in the same right-of-way. Under normal conditions this loss of load is mitigated via operating all 132kv line protection and buss tie breakers in these 132-33/11kv substations normally closed. During a fault POTT and zone selective deferential relaying only trip the breakers immediately in between the faulted line resulting in no loss of transmission supply to power distribution transformers. Distribution feeders are only exposed to a voltage sag of 6 to 20 cycles during normal clearing time. Running these lines normally closed is very advantageous from a service continuity and reliability goals stand point.
The two options being considered are the insertion of a series reactor in each 132kv line bay or the insertion of a phase angle regulator (PAR) on each line.
The only other option is a theoretical relaying system which closes the opened 132kv breaker during a fault and then opens only the breakers between the fault segment like seen during normally closed operation however I have never heard or even seen of such. (Though I do ask if it exists).