zcut123
Electrical
- Feb 25, 2013
- 8
I work in a facility that just recently replaced an old 750 hp dc submarine, (yes submarine) motor.
This dual armature motor was used on a rolling mill, which sees intermittent loading.
basically thin sheets of metal coming through once every 10-15 seconds.
The failed sub motor although rated at 750 hp was being powered by a mg set providing it with approx 75 hp.
What is keeping me up at night is the fact that our management team, replaced it with a 400 hp constant torque motor. Being driven by a 450 hp vfd. Running at 3.5 hz
The no load power being used as per the ABB drives front panel is .25%
When a piece is being processed the power being used never goes above 8%
I can't find effiency curves that even go down that low.
The starting torque is very low in that I can rotate this machine by hand.
My gut tells me this machine is oversized by at least 4 times if not more.
They are convinced that they have done a good thing and are saving money....
I am so incensed by the whole ordeal that I am considering quitting and accepting being unemployed, rather that work in a place that can't seem to get it right.
Did I mention this forced ventilation motor was run for almost two weeks with no cooling. What I noticed when operating like this (with no cooling) is that when the mill became loaded the shaft runout or float seemed severe to me, and the motor growled accordingly. It literally would snap backwards after the piece went through the mill. I didn't notice ANY shaft movement when this was first installed. Now the cooling has been restored, but the float is still present, although not as severe.
I contacted ABB to try and get some clarification and they simply emailed my concerns to the vendor that put this in in the first place. Why would I want to consult with them, when in my opinion they intentionally ignored a basic design criteria for efficiency, which is to match the motor the the load....
Any and all comments are welcomed, and hopefully this forum can put me at ease.
Thanks to all in advance who choose to comment.
This dual armature motor was used on a rolling mill, which sees intermittent loading.
basically thin sheets of metal coming through once every 10-15 seconds.
The failed sub motor although rated at 750 hp was being powered by a mg set providing it with approx 75 hp.
What is keeping me up at night is the fact that our management team, replaced it with a 400 hp constant torque motor. Being driven by a 450 hp vfd. Running at 3.5 hz
The no load power being used as per the ABB drives front panel is .25%
When a piece is being processed the power being used never goes above 8%
I can't find effiency curves that even go down that low.
The starting torque is very low in that I can rotate this machine by hand.
My gut tells me this machine is oversized by at least 4 times if not more.
They are convinced that they have done a good thing and are saving money....
I am so incensed by the whole ordeal that I am considering quitting and accepting being unemployed, rather that work in a place that can't seem to get it right.
Did I mention this forced ventilation motor was run for almost two weeks with no cooling. What I noticed when operating like this (with no cooling) is that when the mill became loaded the shaft runout or float seemed severe to me, and the motor growled accordingly. It literally would snap backwards after the piece went through the mill. I didn't notice ANY shaft movement when this was first installed. Now the cooling has been restored, but the float is still present, although not as severe.
I contacted ABB to try and get some clarification and they simply emailed my concerns to the vendor that put this in in the first place. Why would I want to consult with them, when in my opinion they intentionally ignored a basic design criteria for efficiency, which is to match the motor the the load....
Any and all comments are welcomed, and hopefully this forum can put me at ease.
Thanks to all in advance who choose to comment.