shadowed floor area NFPA 13R 2
dalemontalban
1
In NFPA 13R 2010 section 6.2.3.5.4 mentions of shadowed floor area. How do you figure
a shadowed floor area? I think the answer would depend on 1. size of obstruction
2. distance of obstruction from a wall or sprinkler coverage 2. distance of obstruction from sprinkler.
Am I right?
Thanks.
Dale
Dale,
From your description the way to figure the area is a simple matter in most cases. I've attached a drawing to give an example, each shaded area is a shadow created from spray pattern in the bathroom. To calculate their area is a simple matter of figuring the area of a triangle (
I hope this answered your question.
Jon
If you look in the annex material,A.6.2.3.5.4 states: For purposes of simplified calculations, assume in this theoretical case that the water discharging from a sprinkler travels in a straight line only.
So what Jon says is accurate and it should be a pretty simple calculation, usually a triangle or the sum of some simple geometric shapes.
If you are using any CAD program, just use the area function of the CAD program to determine the value.
I just draw a line from the sprinkler to the edge of the obstruction and project it to the wall. It works pretty easy. I hope the description makes sense.
Travis Mack
MFP Design, LLC
Civic
Are you doing 13 or 13r?????