- Jul 16, 2002
- 4,225
One of our clients had a tree fall on an overhead 12 kV line, breaking two phases. Four spans toward the substation, two conductors of the same phase broke and fell to the ground. We suspected that the initial fault (3300A) caused the phases to slap together on the other span causing a burn down. There wasn't a lot of sag and the conductors were on 8 foot arms, but the phases that burned down were on one side of the pole with 24" spacing.
A strange phenomenon was observed after the fault. There were dozens of small straight pieces of conductor strand scattered around where the second conductor break occurred. See photo at (click on IMG 0387.jpg). Have you seen anything like this? It's like the conductor shattered. The strand ends are not stretched like in a tension break or burnt. The conductor may have been thrashing around on the ground (part asphalt roadway, part concrete sidewalk, part grass) before the fault was cleared.
One theory is that the conductor had experienced overheating in the past and had annealed and become brittle. If this is the case, replacement of all of the conductor may be required. I tend to doubt this theory; the strand I have is not brittle, and according to a Belden glossary, the definition of anneal is:
Weather was 40°F, windy (gusts to 30 mph), cloudy, but no rain or lightning. Conductor is #1/0 ACSR. Total fault clearing time was 32 seconds, with seven apparent instantaneous relay operations and six apparent breaker failures to operate. The relay (ABB IMPRS) fault records are confusing and we are consulting with ABB to make sense of these.
A strange phenomenon was observed after the fault. There were dozens of small straight pieces of conductor strand scattered around where the second conductor break occurred. See photo at (click on IMG 0387.jpg). Have you seen anything like this? It's like the conductor shattered. The strand ends are not stretched like in a tension break or burnt. The conductor may have been thrashing around on the ground (part asphalt roadway, part concrete sidewalk, part grass) before the fault was cleared.
One theory is that the conductor had experienced overheating in the past and had annealed and become brittle. If this is the case, replacement of all of the conductor may be required. I tend to doubt this theory; the strand I have is not brittle, and according to a Belden glossary, the definition of anneal is:
Anneal
To soften and relieve strains in any solid material, such as metal or glass, by heating to just below its melting point and then slowly cooling it. Annealing generally lowers the tensile strength of the material, while improving its flex life and flexibility.
Weather was 40°F, windy (gusts to 30 mph), cloudy, but no rain or lightning. Conductor is #1/0 ACSR. Total fault clearing time was 32 seconds, with seven apparent instantaneous relay operations and six apparent breaker failures to operate. The relay (ABB IMPRS) fault records are confusing and we are consulting with ABB to make sense of these.