VT17
- Apr 27, 2018
- 14
Section 17.2.3 of ACI 318-14 specifies when the overstrength factor is required to be used for design of anchors subject to tensile and shear loading in structures assigned to SDC C, D, E, or F. If I choose to design the anchors for tension only, then I would apply the overstrength factor to determine the design tensile loads per ACI. However, if I choose to use a shear lug to resist the shear loads, should the overstrength factor be applied for the shear lug design?
AISC DG 1 addresses the design of shear lugs and all it mentions is that when AISC Seismic Design Provisions are triggered (i.e. R > 3) then the "column base" can be designed for amplified forces including the amplified seismic load. I interpret "column base" to include shear lug and "amplified load" to be analogous to the actual load times the overstrength factor.
But what about if you choose to use a less detailed intensive LFRS with R </= 3 in a SDC C? I don't see any code that states the overstrength factor should be applied, but if you're designing the column/brace connection to the concrete to ensure the main LFRS is ductile, wouldn't you want the shear lug to also be designed with the overstrength factor?
Please ignore the fact there are other methods to design if the overstrength factor is to be avoided per ACI.
I appreciate your input in advance!