Shear Strength of Concrete Wall

Status
Not open for further replies.

carnahanad

Structural
Feb 4, 2010
44
Hello,

I'm currently reviewing some calculations on a retaining wall. The engineer is checking Vu against (0.5 * Φ * Vc). They are basically using this to say that they don't need shear reinforcement. I always thought that this only applied to concrete beams. For walls and slabs, I just check Vu against (Φ * Vc) to make sure I don't need shear reinforcement. With the other engineers approach, you either end up with some weird stirrups or really thick retaining walls.

Let me know what you guys think.
 
Replies continue below

Recommended for you

For thin elements like slabs or retaining walls you don't need shear reinforcement if the shear is less than phi*Vc.
 
It would be unusual to have shear reinforcement in a retaining wall. Usually the wall is just designed to be adequately thick to work without shear reinforcement.
 
ACI 318-11. 11.9.1 states shear out of plane for walls is to be per slabs in 11.11. 11.4.6.1 states the exception to the 0.5φVc rule for slabs, which I would extend to apply to walls based on 11.9.1.
 
The base and wall both act as beams.

The CRSI Design Handbook uses Vc=phi*2*sqrt(f'c)*12*d, which is compared to factored Vu.
 
Thanks for the discussion on this. I'm going to talk with the original engineer about not using the (1/2) check.
 