Is this allowed as per O86? I didn't think you could use non-full height shear walls and use FTAO?
Is this allowed as per O86? I didn't think you could use non-full height shear walls and use FTAO?
Clause 11.4.1.1 of O86:19 does not allow the sheathing above and below openings to be considered in the shearwall resistance. The way you have coloured the SW pink seems to indicate relying on that sheathing. Per CSA, don't you have to provide holddowns at each end and each side of openings (if required and not offset by gravity loads).But the FTAO walls are full height? If you're able to post the particular clause that concerns you, I might be able to speak to it more directly.
Not sure if OP is practicing in Canada
it would be great to actually be able to use FTAO.
It took about twice the force to rip this sheet at the opening corners.
And that's why CANAM joists are different members for every single member. I feel bad for people who put RTU's on roofs in the future when most of the joists are dialed in on each member, makes it a pain to measure up.It's one of those things where, once you can do fancy stuff, you sort of have to do fancy stuff.