Dear all,
I have one issue in my api 650 storage tank. Due to oversight i have not considered note b in table 5.4a for shell manhole thickness.
I have chosen less thickness than the minimum requirement & mistake come to know when hydro test has been done.
Please give me suggestions for following points:-
1. Is this possible that we can modify the neck thickness or provide other means without replacing manhole ( as per code acceptance)?
2. If we will have to replace the manhole then can we perform box type local hydro test of nozzle only instead of again performing full hydro test? (as per code acceptance)
It will be very helpful if i get any guidelines that needed urgently.
Thank you in advance for support.