I have a situation where a building is being renovated, and the 5th floor has been removed in an area, causing the exterior wall to be unbraced between the fourth floor and the roof (20'). This is an older building, with the walls constructed of clay tile masonry.
At the time I became involved, the contractor had the wall shored at a height of 6'-6" from the fourth floor. The original fifth floor slab was at 8'-10". Due to the fact that the exact construction of the unreinforced clay tile wall isn't known, and I'm not comfortable trying to analyze a wall of such construction, I told the contractor he had to brace the wall at the original height of the fifth floor, and of course he through a fit.
I'm calculating an increase of moment due to wind of approx. 30% due to the shoring height of 6'-6" as opposed to 8'-10". Since I don't know the cross sectional area of the wall and section modulus of the wall, I can't calculate if there will be any net tension on the wall.
I feel like I need to stick to my guns, and make him brace the wall at the original floor height.
Anybody have and other thoughts?
Thanks
I have a situation where a building is being renovated, and the 5th floor has been removed in an area, causing the exterior wall to be unbraced between the fourth floor and the roof (20'). This is an older building, with the walls constructed of clay tile masonry.
At the time I became involved, the contractor had the wall shored at a height of 6'-6" from the fourth floor. The original fifth floor slab was at 8'-10". Due to the fact that the exact construction of the unreinforced clay tile wall isn't known, and I'm not comfortable trying to analyze a wall of such construction, I told the contractor he had to brace the wall at the original height of the fifth floor, and of course he through a fit.
I'm calculating an increase of moment due to wind of approx. 30% due to the shoring height of 6'-6" as opposed to 8'-10". Since I don't know the cross sectional area of the wall and section modulus of the wall, I can't calculate if there will be any net tension on the wall.
I feel like I need to stick to my guns, and make him brace the wall at the original floor height.
Anybody have and other thoughts?