PaultheBigFinn
Electrical
- Dec 16, 2008
- 14
My company designed synchronizing switchgear to bring four 1 mW generators on line to a single bus to supply power to a large hospital's emergency and stand-by systems. We calculated the available fault current from the generators and specified the short circuit withstand rating well above this at 65 kAIC. We did not design the distribution switchgear which coincidentally was also rated 65 kAIC.
A third engineer was hired by the hospital to perform a short circuit analysis of the hospital’s large and fairly complicated power distribution system. They insist that because the ATSs are closed transition, the equipment must be rated for the utility's short circuit contribution as well as the generator's and as such the rating of the switchgear can not be less than 85 kAIC. This in spite of the fact that the time both systems are exposed to each other is less than 100ms for each transition.
Interestingly the SKM modeling software does not have separate model for closed transition ATS, only ATSs in general. The engineer who did the study constructed his own using two switches connected to a common bus.
I found no exception in the code for such a short time, but then there is no discussion of the impact of ATSs either. Is there a precedent for this?
BTW there are ~31 million seconds in a year and if the system was tested and or used once a week the entire exposure time would be about 10 seconds.
Any thoughts would be appreciated.
A third engineer was hired by the hospital to perform a short circuit analysis of the hospital’s large and fairly complicated power distribution system. They insist that because the ATSs are closed transition, the equipment must be rated for the utility's short circuit contribution as well as the generator's and as such the rating of the switchgear can not be less than 85 kAIC. This in spite of the fact that the time both systems are exposed to each other is less than 100ms for each transition.
Interestingly the SKM modeling software does not have separate model for closed transition ATS, only ATSs in general. The engineer who did the study constructed his own using two switches connected to a common bus.
I found no exception in the code for such a short time, but then there is no discussion of the impact of ATSs either. Is there a precedent for this?
BTW there are ~31 million seconds in a year and if the system was tested and or used once a week the entire exposure time would be about 10 seconds.
Any thoughts would be appreciated.