Paulpower
Electrical
- Jul 19, 2008
- 10
Hi,
I am working on a substation project. The transformer is 13.8kv/208v DYn1, secondary solidly grounded. The primary is tapped from 13.8kv overhead line. 13.8kv system is high resistance grounded system.We have ground grid installed around the substation building. Metal clad Substation ground bus and secondary 208V neutral are bond to ground grid. The 13.8 kv overhead phase conductors are accompanied by a ground wire on the messenger line.
The directly buried 3c 13.8kv cable includes an integral bare ground conductor. If I use an outdoor cold shrink termination with a boot of 3 breakout for 3 phase conductors to tap from overhead line, shall I weld the cable shield to the integral ground conductor, then bond them to ground wire on overhead line? Generally, what shall I do on the other end of the cable which enter the metal enclosure of substation? Do I have to bond the ground conductor in the 13.8kv cable to the unit substation grond grid? Do I need to install a separate bare copper ground conductor with the cable when I bury the cable in a PVC conduit?
I am puzzled by the groud concept, please recommend some reference document also.
Thanks in advance.
I am working on a substation project. The transformer is 13.8kv/208v DYn1, secondary solidly grounded. The primary is tapped from 13.8kv overhead line. 13.8kv system is high resistance grounded system.We have ground grid installed around the substation building. Metal clad Substation ground bus and secondary 208V neutral are bond to ground grid. The 13.8 kv overhead phase conductors are accompanied by a ground wire on the messenger line.
The directly buried 3c 13.8kv cable includes an integral bare ground conductor. If I use an outdoor cold shrink termination with a boot of 3 breakout for 3 phase conductors to tap from overhead line, shall I weld the cable shield to the integral ground conductor, then bond them to ground wire on overhead line? Generally, what shall I do on the other end of the cable which enter the metal enclosure of substation? Do I have to bond the ground conductor in the 13.8kv cable to the unit substation grond grid? Do I need to install a separate bare copper ground conductor with the cable when I bury the cable in a PVC conduit?
I am puzzled by the groud concept, please recommend some reference document also.
Thanks in advance.