OP here. I'm not able to edit the original post, but I'll try to explain what I mean. Here are the steps I have done:
1. I calculated the allowable pile capacity using Excel, using the alpha method (weak clay). I got:
Allowable Capacity = 548 KN
2. Since the piles are 2.5 diameter close to each other, I calculated the Group Efficiency using Los Angeles method. I got Reduced Allowable Capacity = 453.59 KN.
3. I estimated the pile to be a point spring using the silly equation everyone is using ( K = EA/L, E from concrete). I'm not enthusiastic to treat the pile stiffness as coming only from concrete since I have no rock at the bottom, but I have no time currently to investigate more into better equation. I modeled the structure in CSI Safe using the point springs.
4. I got the max pile reaction to be 460.89 KN, exceeding the Reduced Allowable Capacity (Reduced due to Group effect) but less than single pile allowable capacity. My question is: Are the piles OK? My engineering feeling is mixed: not all piles are that much stressed in a local neighberhood. Say one pile is stressed beyond the group-max-allowed capacity but the 4 piles around it are stressed for less.
To reword more my question, shall I judge a single pile for exceeding the group efficiency or should I average down local groups of 4 (2 x 2) for the comparison?