bennyvw
Electrical
- Oct 10, 2022
- 2
I'm currently modeling my 11kV distribution network in ETAP with a number of lumped loads representing the large motor installation base at the site.
As part of my protection coordination study I've found that some of the feeder protection devices are tripping as a result of fault currents from motor contribution.
I'm unclear on how ETAP models motor contribution to short circuit fault current, does it assume a constant contribution for the duration of the fault? Or does it decay quickly as is the case in reality?
My trip times on these relays are in the order 1-2 seconds at these fault levels. I would have assumed at that point the motor contribution to short circuit fault current would be negligible. Can these trips be ignored? Or should I turn off motor contribution in ETAP?
As part of my protection coordination study I've found that some of the feeder protection devices are tripping as a result of fault currents from motor contribution.
I'm unclear on how ETAP models motor contribution to short circuit fault current, does it assume a constant contribution for the duration of the fault? Or does it decay quickly as is the case in reality?
My trip times on these relays are in the order 1-2 seconds at these fault levels. I would have assumed at that point the motor contribution to short circuit fault current would be negligible. Can these trips be ignored? Or should I turn off motor contribution in ETAP?