Skogsgurra
Electrical
- Mar 31, 2003
- 11,815
Hi,
Long time no type.
Anyone that knows anything about starting a Siemens Synchronous motor on a weak mains. Motor data: 11,5 kV 9 MW, P.F.-controller sets excitation current. We experience starting times longer than 20 seconds, which trips the circuit breaker. Adding more Mvar does not seem to help. Voltage drops from a low 11,3 kV to a low-low 10,4 kV.
We are waiting for "better" voltage. Anything that can be done else?
Long time no type.
Anyone that knows anything about starting a Siemens Synchronous motor on a weak mains. Motor data: 11,5 kV 9 MW, P.F.-controller sets excitation current. We experience starting times longer than 20 seconds, which trips the circuit breaker. Adding more Mvar does not seem to help. Voltage drops from a low 11,3 kV to a low-low 10,4 kV.