galvani
Electrical
- Apr 12, 2002
- 1
I use a PLC with 0-10v analog inputs. My devices (pressure transducers) have a 4-20 ma output. To convert, I put a 500 ohm resistor inline with my signal to generate a voltage drop. This results in a signal of 2-10v proportional to the ma signal. This works fine for my application, but I am cutting off some of my resolution.
Now the question...
Shouldn't I be able to use an OP AMP instead of the resistor workaround to generate a true 0-10v signal from my ma device? It seems as if I should be able to set an OP AMP up as a difference amp with my device on one input and a constant 4 ma siganl on the other. Since the output of the OP AMP should then be proportional to the DIFFERENCE between the two signals, I should get 0 - 10 v output (with an appropriately sized feedback resistor).
I should, but I can't get this to work in my mock-ups. Any ideas? Is there a better way to do this?
Thanks,
g
Now the question...
Shouldn't I be able to use an OP AMP instead of the resistor workaround to generate a true 0-10v signal from my ma device? It seems as if I should be able to set an OP AMP up as a difference amp with my device on one input and a constant 4 ma siganl on the other. Since the output of the OP AMP should then be proportional to the DIFFERENCE between the two signals, I should get 0 - 10 v output (with an appropriately sized feedback resistor).
I should, but I can't get this to work in my mock-ups. Any ideas? Is there a better way to do this?
Thanks,
g