Hi all,
Our client's medium voltage switchgear specifications indicated an ESD Relay which is SIL (Safety Integrity Level) rated and operates at 24 VDC with N.O. output contact (suitably rated at 125Vdc) wired to energize the trip coil which draws 3.5A at 125Vdc. The Process ESD system energizes the ESD relay which in turn closes its output contacts to energize the circuit breaker trip coil. The ESD relay is installed INSIDE the 13.8 kV switchgear.
The problem started when we discovered that the specified ESD relay's (which is SIL-rated)output contacts are not rated or suitable to make or break the circuit breaker trip coil as officially confirmed by the relay manufacturer.
As Electrical folks, we recommended two things:
1. Remove the ESD relays from the switchgear and install it inside an interposing relay panel. Install a standard switchgear rated trip relay, device 94T (ABB RXMH-2 or AREVA MVAJ type) whose coil will be operated by the ESD relay at 125VDC and whose output contacts will energize the circuit breaker trip coil at 125Vdc.
OR
2. Relace the ESD relay with a TRIP relay (ABB RXMH-2 or AREVA MVAJ type) operated at 24VDC and whose output contacts will energize the circuit breaker trip coil at 125Vdc.
My only dilemna is that our Instrument & Control Group (I&C) might require us that the TRIP relay should be SIL rated. The ABB RXMH-2 and AREVA MVAJ are note SIL rated and we could not find a standard TRIP relay that is SIL rated.
As Electrical practitioner, I should ensure that the relay that operates the circuit breaker has contacts that is rated for the purpose and duty. A standard TRIP relay is rated for such duty and I believe that any component that DIRECTLY control and operate the switchgear circuit breaker should comply with Electrical and switchgear manufacturing standards. Secondly, it is also my belief that SIL rating should looked at as an overall control system and should not be "prescriptive" but quantitative based on failure rates, reliability and availability of the ESD as a SYSTEM. This means, the TRIP relay which is operating the breaker and installed inside the switchgear MAY NOT necessarily be SIL rated per se. The interposing relay (ESD) or signal source that operates the TRIP relay can be SIL rated as they like but the battery limit should be drawn on the switchgear in terms of suitability and reliability to DIRECTLY operate the circuit breaker. Is there a trip relay (standard device 94) which is SIL rated in the market?
I am expecting a tight discussion on the above dilemna but I am hoping some subject matter experts in this forum can provide me their thoughts and suggestions especially if they have the same experience in the past.
I thank you in advance for any ideas that will be given.
Our client's medium voltage switchgear specifications indicated an ESD Relay which is SIL (Safety Integrity Level) rated and operates at 24 VDC with N.O. output contact (suitably rated at 125Vdc) wired to energize the trip coil which draws 3.5A at 125Vdc. The Process ESD system energizes the ESD relay which in turn closes its output contacts to energize the circuit breaker trip coil. The ESD relay is installed INSIDE the 13.8 kV switchgear.
The problem started when we discovered that the specified ESD relay's (which is SIL-rated)output contacts are not rated or suitable to make or break the circuit breaker trip coil as officially confirmed by the relay manufacturer.
As Electrical folks, we recommended two things:
1. Remove the ESD relays from the switchgear and install it inside an interposing relay panel. Install a standard switchgear rated trip relay, device 94T (ABB RXMH-2 or AREVA MVAJ type) whose coil will be operated by the ESD relay at 125VDC and whose output contacts will energize the circuit breaker trip coil at 125Vdc.
OR
2. Relace the ESD relay with a TRIP relay (ABB RXMH-2 or AREVA MVAJ type) operated at 24VDC and whose output contacts will energize the circuit breaker trip coil at 125Vdc.
My only dilemna is that our Instrument & Control Group (I&C) might require us that the TRIP relay should be SIL rated. The ABB RXMH-2 and AREVA MVAJ are note SIL rated and we could not find a standard TRIP relay that is SIL rated.
As Electrical practitioner, I should ensure that the relay that operates the circuit breaker has contacts that is rated for the purpose and duty. A standard TRIP relay is rated for such duty and I believe that any component that DIRECTLY control and operate the switchgear circuit breaker should comply with Electrical and switchgear manufacturing standards. Secondly, it is also my belief that SIL rating should looked at as an overall control system and should not be "prescriptive" but quantitative based on failure rates, reliability and availability of the ESD as a SYSTEM. This means, the TRIP relay which is operating the breaker and installed inside the switchgear MAY NOT necessarily be SIL rated per se. The interposing relay (ESD) or signal source that operates the TRIP relay can be SIL rated as they like but the battery limit should be drawn on the switchgear in terms of suitability and reliability to DIRECTLY operate the circuit breaker. Is there a trip relay (standard device 94) which is SIL rated in the market?
I am expecting a tight discussion on the above dilemna but I am hoping some subject matter experts in this forum can provide me their thoughts and suggestions especially if they have the same experience in the past.
I thank you in advance for any ideas that will be given.