Dear All,
I am in the process of developing a spreadsheet and would appreciate help on the following topic:
In case of a high pressure safety valve, say boiler superheater PSV, the flow is choked at vent exit as well as at PSV nozzle opening just like in the example given in Nonmandatory Appendix II of ASME B31.1.
If a silencer has to be added to the mentioned configuration, it starts to get puzzling to me.
For argument sake, the vent exit static pressure (without a silencer) is calculated to be 50 psia.
Now, if I add the silencer to existing vent piping, what do I do? Should I just tell the vendor to design the silencer for 35.3 psid(50-14.7)for the calculated flow, temperature, pressure and be done with it? Or am I totally wrong? Sorry for poor English. I would appreciate any insight.
Thanks