I've read at least (2) past posts regarding "Crushing of Plywood" and "Wood Bearing Plate at Trusses".
Now what about sill plate crushing at heavy girder reactions?
After reading the prior threads, i can be comfortable with a slight over-stress of perpendicular compression. But when i have a 16K reaction bearing on a 3.5x3.5 parallam, the compression perp exceeds 1,000 psi! I don't want to ignore that!
With one commercial general contractor, for over a decade, i've been specifying that the column shall interrupt both the top plates and sill plate and bear on a steel plate on concrete foundation wall. I've had no problem with that contractor. Did they actually comply in the field? As reputable as they are, i trust they do.
A different contractor, for a multi-family developer, is questioning this specification. After meeting and hearing my defense, they do understand and will comply for at least one particular heavy reaction location. Desiring to please the client, i am considering to raise my threshold of compression perp, but i must stay within reason.
After reading the aforementioned posts, i can conclude that crushing, WITHIN REASON, is not a major issue. But, where is that threshold? Do i accept nothing higher than 425 for SPF and likewise 625 for DFL or how much can i be comfortable exceeding this?
Related to this topic, in a prior post, i inquired, without a reply:
If the wood actually DID begin to crush, wouldn't the allowable compression perpendicular actually increase as the wood is crushing, and thus, soon terminate the crushing? Any opinions?
Another consideration is that if crushing DID occur, if brittle finishes, such as gypsum, are on that wall, cracking of that finish will also occur.
Another other thoughts?
Thank you!
Now what about sill plate crushing at heavy girder reactions?
After reading the prior threads, i can be comfortable with a slight over-stress of perpendicular compression. But when i have a 16K reaction bearing on a 3.5x3.5 parallam, the compression perp exceeds 1,000 psi! I don't want to ignore that!
With one commercial general contractor, for over a decade, i've been specifying that the column shall interrupt both the top plates and sill plate and bear on a steel plate on concrete foundation wall. I've had no problem with that contractor. Did they actually comply in the field? As reputable as they are, i trust they do.
A different contractor, for a multi-family developer, is questioning this specification. After meeting and hearing my defense, they do understand and will comply for at least one particular heavy reaction location. Desiring to please the client, i am considering to raise my threshold of compression perp, but i must stay within reason.
After reading the aforementioned posts, i can conclude that crushing, WITHIN REASON, is not a major issue. But, where is that threshold? Do i accept nothing higher than 425 for SPF and likewise 625 for DFL or how much can i be comfortable exceeding this?
Related to this topic, in a prior post, i inquired, without a reply:
If the wood actually DID begin to crush, wouldn't the allowable compression perpendicular actually increase as the wood is crushing, and thus, soon terminate the crushing? Any opinions?
Another consideration is that if crushing DID occur, if brittle finishes, such as gypsum, are on that wall, cracking of that finish will also occur.
Another other thoughts?
Thank you!