- Sep 23, 2003
- 27
Administration kills engineering. Design calculation ability is a muscle, if not trained it atrophies...
I am curently designing a mobile generator unit in a closed area.I need to determine the amount of air flow requiered to maintain an ambiant temp of no more than 40ºc.
Known:
desired ambiant temp: 40ºc
outside temp (cooling air) :up to 30ºC
kw regected by components inside habitacle :205Kw
unknown:
air flow volume needed in order to maintain ambiant temp at no more than 40ºc in order to select exhaust fan and inlet damper/loovers?
air speed could reach up to 1000ft/min
I need reminding of practical equations/formulas and basic notions?
I am curently designing a mobile generator unit in a closed area.I need to determine the amount of air flow requiered to maintain an ambiant temp of no more than 40ºc.
Known:
desired ambiant temp: 40ºc
outside temp (cooling air) :up to 30ºC
kw regected by components inside habitacle :205Kw
unknown:
air flow volume needed in order to maintain ambiant temp at no more than 40ºc in order to select exhaust fan and inlet damper/loovers?
air speed could reach up to 1000ft/min
I need reminding of practical equations/formulas and basic notions?