Simple diaphragm with interior wall interruption 2
StrEng007
543
This post is a follow-up to this thread:
I'd like to treat this 2 part diaphragm as a single diaphragm, where the shears at each side of the boundary party wall cancel each other out. In order to do so, I need to make sure I get the shears into the party wall to create the location in which I can cancel out the shear demand at that interface.
How do I determine the forces at this location? Wouldn't it be the same as the shear flow for the chord force using the overall building length?
Putting some numbers to it:
Transverse Load = 100 lb/ft
B = 50 FT
L = 30 FT
Chord force = (100 lb/ft) (50 FT)²/(8x 30FT) = 1041.67 lb
Shear, V = (100 lb) x (50 FT)(1/2) = 2500 lb
Unit shear, v = 2500 lb/30 FT = 83.33 lb/ft
Note, unit shear is same as shear flow of the chord = Chord/(0.25B) = 83.33 lb/ft
That is, if you take the total area under the shear flow linear distribution, you get the chord force in the overall diaphragm.
So is this to say that the shear located on each side of the party wall is 83.33 lb/ft as shown below?
That would keep equal and opposite forces in equilibrium when considering each half of the diaphragm.
If not, what is the shear demand each side of the party wall at B?
Hi StrEng007,
If I understand your question correctly, you are trying to consider the two separate diaphragm as one (with the combined depth of L=30ft) so that the chord force is smaller.
I would personally use the shear flow equations (q = VQ/I) rather than using the chord forces to design the connections at the party wall. The former is more theoretically sound.
I find it a little hard to follow your calculation above. Are you using the complementary property of shear stress (i.e. tau_xy = tau_yx) to justify designing for the 83.3 lbs/ft? How does chord force (a normal force) play into the shear flow calculation?
The equation I show for the 83.3 lb/ft is the result of my theoretical shear flow equation applied to the entire building (diaphragm as a whole).
Instead of using the formula q=VQ/I, I'm basically recognizing that q=83.3 lb/ft
The proof is taking the area under the shear flow diagram:
So I'm basically saying, isn't the shear flow at the location where diaphragm 1 meets the party wall parapet, 83.3lb/ft which is equal and opposite to the diaphragm that connects to the opposite face of that parapet?