Let me first preface this by saying I am a jr. bridge engineer and have zero experience with this type of connection. We are attempting to hang a "fascia panel" in one of the spans of our bridge to make up for the drastic difference in superstructure depth. The adjacent spans have 6' deep beams while this span has only 3' deep beams. Span is ~70' long. Therefore, we will be using a FRP panel that is 3.5' tall in order to line up at the bottom of the 6' beams and will cover a portion of bottom flange of the 3' beams. I have attached drawings so see those. I am trying to come up with the structural support for this FRP Panel system. I have a 16x16x1/2 HSS in order to limit deflections. I am having trouble with connecting the HSS to the pier. I wanted to use the Simple Shear Unstiffened Seat Connection that I am finding in my steel manual for simplicity. AISC LRFD 2nd Edition 9-128. A few things:
1. I purposely made the angle only 8" long to keep the edge distance for the anchor rod and angle small. I have a lot of reinforcing in that portion of the pier so I need to have the 6-5/8" min. dimension I am showing. I cant find any examples where the seat is not at least the width of the beam. Is this feasible? Is there any maximum edge distance requirement that I would violate if I kept the anchor rods in same place but made the angle extend the full 16"?
2. My plan for the HSS to angle connection was going to be slotted holes to allow for the expansion. However after further reading here it seems that slotted holes are not a good idea for expansion (sometimes okay if loads are very small). Is this true even if my loading is normal to the slot? My loads seem fairly small (Service Reaction around 3.5 kips). The HSS is only supporting itself and the panel. Is there maybe a better way to go about this.
Any help would be much appreciated as I said I am really struggling with this one.
1. I purposely made the angle only 8" long to keep the edge distance for the anchor rod and angle small. I have a lot of reinforcing in that portion of the pier so I need to have the 6-5/8" min. dimension I am showing. I cant find any examples where the seat is not at least the width of the beam. Is this feasible? Is there any maximum edge distance requirement that I would violate if I kept the anchor rods in same place but made the angle extend the full 16"?
2. My plan for the HSS to angle connection was going to be slotted holes to allow for the expansion. However after further reading here it seems that slotted holes are not a good idea for expansion (sometimes okay if loads are very small). Is this true even if my loading is normal to the slot? My loads seem fairly small (Service Reaction around 3.5 kips). The HSS is only supporting itself and the panel. Is there maybe a better way to go about this.
Any help would be much appreciated as I said I am really struggling with this one.