simple transformer dc

Status
Not open for further replies.

foretmark

Electrical
Jul 14, 2008
28
In order to get 24VDC using a transformer, I'd like to take a 16v transformer, rectify it and put a capacitor across the lumpy DC (after the rectifier of course). Obviously using a 24v transformer, I'll end up with almost 40VDC. For a 100VA transformer, I have roughly 4a available to me at 24v, and 6a at 16v. By using the cap, after the rectifier, do I still have the 6 Amps available at ~24V?

 
Replies continue below

Recommended for you

Have you ever heard of conservation of energy?

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
6A at about 24V is approx 144W. Do you think your 100VA transformer is going to be happy about that?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
ok, IAC=1.8 x IDC for a FWB. So as long as my load doesn't exceed 3.5A or so, I should be ok...thanks
 