S020
Structural
- Jan 6, 2019
- 3
Hi All,
I am yet to see a thread addressing these formalised changes yet so I thought I would put some thoughts to paper and see if anyone has further comments.
One of the limitations of the simplified method is that axial stress be kept to 3MPa max unless reinforcement is provided on both faces. So if I spec. equally distributed reinforcement on two faces of a wall I am permitted to push wall stresses beyond 3MPa. Is there a hard limit? When do I get forced to start designing walls as a column with this method? Does my wall become impractically thick to compete against the contribution of compression steel that is restrained? But then again, proposing to lig long runs of walls for 20 storeys will never win you a job ever again.
If a wall sees any tension through its section it needs to be designed using strut tie if H/L<=2? Surely not. Every wall in a highrise tower wall (or even worse - a small 4 storey walk-up) requires its own deep beam model, when summated would result in hours of work to simply check if sizes are correct let alone reinforcement. This seems taxing and a little too punishing balanced against the professional fees a consultancy will price for a low-rise building. Is there no other way around this? Perhaps compute the compressive stresses P/A + M/Z and use the simplified method to calculate the compressive resistance? Shear walls used to be permitted to be designed per section 8 i.e. flexural beams in the 2009 code. What happened?!
Restraint of vertical reinforcement - for walls exceeding 50MPa we need to detail to 14.5.4 which by my own interpretation reads: provide ligatures to all longitudinal reinforcement for a distance the greater of the length of the wall or 1/6 the clear height. Take a 2800 long shear wall that has a clear height of 2800 between connecting slabs - I have to provide ligatures over its entire height i.e. I am designing what looks like a column if my concrete grade exceeds 50MPa. Is my interpretation correct?
There appears to be a complete lack of reference to the new detailing requirements of section 14.6 limited ductile walls in section 11. Surely there needs to be some wording added to the scope of section 11 to reference the requirements of 14.6? Someone has / is going to produce a non-compliant design. It looks like unrestrained ends of shear walls will be forced to include ligatures within termed boundary elements where the compressive stresses exceed 0.15F'c. Easy enough.
To summarise:
Max compressive stress for two sided reinforced wall (no tension) = ?
F'c > 50MPa = ligs required. it's pretty much a column if you're designing shear walls.
any tension = non-flexural
P/A + M/Z compressive zone stress > 0.15F'c = provide ligs (earthquake provision)
Anything I've missed or misinterpreted?
S020
I am yet to see a thread addressing these formalised changes yet so I thought I would put some thoughts to paper and see if anyone has further comments.
One of the limitations of the simplified method is that axial stress be kept to 3MPa max unless reinforcement is provided on both faces. So if I spec. equally distributed reinforcement on two faces of a wall I am permitted to push wall stresses beyond 3MPa. Is there a hard limit? When do I get forced to start designing walls as a column with this method? Does my wall become impractically thick to compete against the contribution of compression steel that is restrained? But then again, proposing to lig long runs of walls for 20 storeys will never win you a job ever again.
If a wall sees any tension through its section it needs to be designed using strut tie if H/L<=2? Surely not. Every wall in a highrise tower wall (or even worse - a small 4 storey walk-up) requires its own deep beam model, when summated would result in hours of work to simply check if sizes are correct let alone reinforcement. This seems taxing and a little too punishing balanced against the professional fees a consultancy will price for a low-rise building. Is there no other way around this? Perhaps compute the compressive stresses P/A + M/Z and use the simplified method to calculate the compressive resistance? Shear walls used to be permitted to be designed per section 8 i.e. flexural beams in the 2009 code. What happened?!
Restraint of vertical reinforcement - for walls exceeding 50MPa we need to detail to 14.5.4 which by my own interpretation reads: provide ligatures to all longitudinal reinforcement for a distance the greater of the length of the wall or 1/6 the clear height. Take a 2800 long shear wall that has a clear height of 2800 between connecting slabs - I have to provide ligatures over its entire height i.e. I am designing what looks like a column if my concrete grade exceeds 50MPa. Is my interpretation correct?
There appears to be a complete lack of reference to the new detailing requirements of section 14.6 limited ductile walls in section 11. Surely there needs to be some wording added to the scope of section 11 to reference the requirements of 14.6? Someone has / is going to produce a non-compliant design. It looks like unrestrained ends of shear walls will be forced to include ligatures within termed boundary elements where the compressive stresses exceed 0.15F'c. Easy enough.
To summarise:
Max compressive stress for two sided reinforced wall (no tension) = ?
F'c > 50MPa = ligs required. it's pretty much a column if you're designing shear walls.
any tension = non-flexural
P/A + M/Z compressive zone stress > 0.15F'c = provide ligs (earthquake provision)
Anything I've missed or misinterpreted?
S020