Thanks to everyone for your thoughtful replies.
Just to let you know what my other research has provided:
The CISC responded with:
"From an erection consideration perspective, 2 bolts are the minimum required for installation purposes. Within the industry, there has always been a general rule of 2 bolt minimum for any structural connection."
However, the reply I got from the AISC referred to OSHA standards:
"You will want to check the Federal Register, as OSHA does have some rules regarding the number of bolts that must be in place before a structural member can be released from the hoisting lines (Section 1926.756). The Register can be obtained from
Note that the Register does disntiguish between standard beams and columns and bracing members. You may be able to use a single bolt in bracing members."
More specifically (Direct from OSHA):
1926.756 Beams and columns.
(a) General. (1) During the final placing of solid web structural members, the load shall not be released from the hoisting line until the members are secured with at least two bolts per connection, of the same size and strength as shown in the erection drawings, drawn up wrench-tight or the equivalent as specified by the project structural engineer of record, except as specified in paragraph (b) of this section.
(2) A competent person shall determine if more than two bolts are necessary to ensure the stability of cantilevered members; if additional bolts are needed, they shall be installed.
(b) Diagonal bracing. Solid web structural members used as diagonal bracing shall be secured by at least one bolt per connection drawn up wrench-tight or the equivalent as specified by the project structural engineer of record.
So basically, OSHA is fine with a single bolt connection for diagonal bracing only. But having read what krus1972 wrote, I will be specifying two-bolt connections even for braces.
Thanks again to everyone