SilverfoxUK
- Jun 21, 2018
- 62
I’ve got to take about 600A from a 500kVA transformer. The calcs are taking me to 300mm singles or 400mm 4c.
400mm I can’t accommodate the bending radius so that’s out. The gland plate on the transformer is mild steel so with the singles I’m on route to creating a large induction cooker.
My spec called for a non-ferrous gland plate but getting past an existing cable on the gland plate is proving problematic.
The smaller cable to the back of the terminal box will be disinvested.
My get out of jail is to run the 3 x phase cores as close as possible in the existing mild steel gland plate and then cut slots between the holes. Has anyone had experience with this?
Slot size, 1mm, 5mm, larger ??
Could you backfill the slot with mastic of lead?
Would welcome the benefit of your experience.