Single floor Fire Protection system

Status
Not open for further replies.

VVhope

Mechanical
Jun 1, 2023
6
Hi All,

I have a building with only ground floor with area 180m X 24m and the building is unsprinklered building. I am performing hydraulic calculations. I am thinking to perform as horizontal standpipe system as I need three fire hose cabinets for the building. I believe it is okay to use horizontal standpipe system, just want to make sure. I am new to fire protection engineering. Any suggestions would help.
 
Replies continue below

Recommended for you

You need to start by determining what is required based on the building code, local amendments and AHJs direction. For Class I standpipe hose connections on horizontal exits refer to NFPA 14-2019 7.3.2.2.1 and IFC-2018 905.4. There's a lot more to it but that will get you started.

Where is the project location and what codes/standards are you following?
 