Could someone please explain to me why when a device is tied into a three phase panel, and is fed with a two pole breaker, why is that device refered to as a single phase 208? From my understanding, it is drawing from two of the three phases 120 degrees from one another. Thanks for any assistance.
 
Replies continue below

Recommended for you

If you have just two wires, the voltage between the two wires is a single value, regardless if the source is one-phase or three-phase. There is no way to determine, by measuring the single voltage, that it originated from 3-phase source. It appears and in fact is one and the same as a voltage from a single-phase source.

If you add a neutral to the circuit, then you could argue that it should be called 2-phase. But 2-phase is usually intended for sources that are 90 degrees out of phase rather than 120 - and is fairly unusual in power systems.
 
A phase is not a single conductor or reference point. Phases require two points either usually Line and Line. A 1-phase system has 1 set of L-L conductors, a 3-phase system has 3 possible sets of L-L conductors, and the very rare 2-phase system has 2 sets of L-L.

You probably don't refer to a household range as a 2-phase device even if it is connected to (2) hot conductors. So when describing a single phase transformer, instead of saying "it is drawing from two of the three phases" say it is drawing from 2 of the 3 line conductors and see if it is easier to explain.
 