Plinko
Electrical
- Oct 29, 2001
- 12
I'm looking at several different fault current tables for single phase XFRs and I see several different values for similar sizes and %Z. Three phase calcs seem straight forward (i.e. 3P bolted fault for a 500kVA 277/480 5%Z is about 12,028 amps). I have a table in front of me saying that a 1P XFR 15kVA 120/240 1.6%Z is 5456 amps L-G fault...My calculation shows to be 7813 Amps...I've seen table that show my calculation to be right as well....
WHAT AM I MISSING HERE?
Thanks in advance.
WHAT AM I MISSING HERE?
Thanks in advance.