richanton
Electrical
- Jul 15, 2002
- 128
We have been mulling around an apparent problem with UPS designs. We generally always use industrial UPS's with single phase output at 120 volts going to a circuit breaker panel. The question that came up is that there is not enough short circuit to trip a branch breaker on the panelboard. This issue is even more noticeable on a European system that has 230 volts, single phase as the output voltage. I read a prior post on the subject that implies that the response of the UPS when it sees a fault on an output branch breaker is to switch to the bypass mode, under which normal system short circuit would be available. This is all somewhat confusing. What I am trying to figure out is once the UPS does transfer to the bypass system, what will trip first, the branch breaker or the main breaker at the output of the UPS. Do I just treat both breakers as if it was a normally coordinated system, or is there some other factor involved.