Mar 8, 2009 #1 samreen Electrical Aug 27, 2007 10 PK why synch check is bypass in single pole auto reclosing?
Mar 8, 2009 #2 davidbeach Electrical Mar 13, 2003 9,464 US Why not? What will be out of synch? Upvote 0 Downvote
Mar 8, 2009 Thread starter #3 samreen Electrical Aug 27, 2007 10 PK Normally we bypass synch check in single pole auto reclosing.. Upvote 0 Downvote
Mar 9, 2009 #4 slavag Electrical May 15, 2007 2,038 IL Hi Samreen As David wrote: Why not. One-phase trip is open only one pole, you don't loss synch with grid , you still have two phases. Best Regards. Slava Upvote 0 Downvote