Electrical
- Sep 24, 2003
- 4
A small but welcomed reply would be most helpful in this matter!
According to my calculations, the size transfomers required for a 120 - 240 volt 3 phase service of 1200 amps (max rated load) should be three (3) 167 KVA transfomers!
Now if I consider 80% of full load (960 amps)I will wind up with appx a 133 kva rating for a set of transfomers. This will not be possible In as much as they don't make any pole mount transfomers in between 100 kva and 167 kva unless special ordered or in three phase padmount confuguration.
Anyway, I would like to check my figures to see if I am right! Thanks