Hi everybody. I want to size a stand-by diesel generator for a plant and I need a bit of help here
The final steady-state load is 750KVA, 630KW, 1100A. Derating Factor in the location is 12%.
My main concern is that this diesel generator should be able to start an electric motor that has a heavy starting current, even with a soft starter.
The starting current is 2220A and the starting time is 37 seconds. But after the motor started, it draws about 300A.
Considering that this motor should be started when the load on diesel is 500A already, the diesel generator should be able to provide (2220+500=2720 A) for 37 seconds.
Can I choose a 1MVA (1443A) diesel generator and hope that generator could be overloaded in starting part with no problem, or should I choose a 2MVA (2886A) diesel generator for this purpose?
Also, do I have to consider the derating factor (12%) and safety margin (10%) for the starting part? In this case, I have to choose a 2.5MVA for this plant.
Thanks
The final steady-state load is 750KVA, 630KW, 1100A. Derating Factor in the location is 12%.
My main concern is that this diesel generator should be able to start an electric motor that has a heavy starting current, even with a soft starter.
The starting current is 2220A and the starting time is 37 seconds. But after the motor started, it draws about 300A.
Considering that this motor should be started when the load on diesel is 500A already, the diesel generator should be able to provide (2220+500=2720 A) for 37 seconds.
Can I choose a 1MVA (1443A) diesel generator and hope that generator could be overloaded in starting part with no problem, or should I choose a 2MVA (2886A) diesel generator for this purpose?
Also, do I have to consider the derating factor (12%) and safety margin (10%) for the starting part? In this case, I have to choose a 2.5MVA for this plant.
Thanks