Badbird2000
Mechanical
- Jun 15, 2010
- 20
Ok kids, hold on to your hats...
I am working on a 4 story science and mathmatics building for a local college. The system will consist of rooftop units with chilled water coils and pre-heat coils, chillers, boiler, pumps etc, with vav boxes serving the classrooms and offices. In trying to size the pre-heat coil, my intent is maintain a minimum discharge air from the unit around 55 degrees F and do heating in the spaces with reheat coils in the vav boxes. My question is, if you take a cold morning at design heating conditions, 9 degrees F, i am assuming (and that's not always a good thing) my boxes are going to be at the minimum setting, roughly 30% of my total cfm for cooling. So, i would not have the maximum airflow across the coil, mixed with the return air from the unit. In some cases, my o.a. is more than the minimum 30% airflow, so i would have to have 100% o.a. to maintain my ventilation rates. So, would i hvae to size the coil for 100% of my o.a. at 9 degrees at that point?
For example, RTU-2 has a maximum airflow of 9,500 cfm and an o.a. of 3950. 30% of the maximum is 2,850 but i need 3950 to maintain my ventilation. Would i assume it's going to see 3,950 of 9 degree air and size the pre-heat for that condition?
Any help? Am i making this harder than it needs to be?
Wayne
I am working on a 4 story science and mathmatics building for a local college. The system will consist of rooftop units with chilled water coils and pre-heat coils, chillers, boiler, pumps etc, with vav boxes serving the classrooms and offices. In trying to size the pre-heat coil, my intent is maintain a minimum discharge air from the unit around 55 degrees F and do heating in the spaces with reheat coils in the vav boxes. My question is, if you take a cold morning at design heating conditions, 9 degrees F, i am assuming (and that's not always a good thing) my boxes are going to be at the minimum setting, roughly 30% of my total cfm for cooling. So, i would not have the maximum airflow across the coil, mixed with the return air from the unit. In some cases, my o.a. is more than the minimum 30% airflow, so i would have to have 100% o.a. to maintain my ventilation rates. So, would i hvae to size the coil for 100% of my o.a. at 9 degrees at that point?
For example, RTU-2 has a maximum airflow of 9,500 cfm and an o.a. of 3950. 30% of the maximum is 2,850 but i need 3950 to maintain my ventilation. Would i assume it's going to see 3,950 of 9 degree air and size the pre-heat for that condition?
Any help? Am i making this harder than it needs to be?
Wayne