sizing boiler headers 2

Status
Not open for further replies.

Prestz

Mechanical
Aug 12, 2008
12
0
0
Is it rigth sizing a header boiler with velocity of steam 3000 fpm?
what is the correct velocity in a header boiler according code?
thanks
 
Replies continue below

Recommended for you

there are 2 interpretations of "header".

For the case of a "header type boiler config" , the "header' is the common steam transfer pipe from the multiple boilers to the steam user. In that case, the header size is based on limiting the frictional pressure drop and /or noise , vibration and wet steam erosion/corrosion. For frictional pressure loss, you would first define the allowable pressure drop ( 3% of inlet pressure, for example), and then calculate the frictional pressure drop for various pipe sizes, and select the smallest pipe size that also meets the noise and vibration limits. The noise and vibration limits might require the the max velocity not be greaer than ( 15% ) soundspeed.

The other interpretation of the term "header" is the large distribution /collection pipe that feeds steam to the individual heat exchangers in the boiler, such as for example the primary superheater. That header is sized to limit the tube to tube flow unbalance to the ensemble of tubes in the heat exchanger, so that the tube to tube temperature unbalance at the outlet of the heat exchanger is below allowable metallurgical limits. That sizing calculation is a bit more complicated to describe, and not as easily summarized as the first header term.
 
Saturated steam Boiler leads are normally sized for 6000 - 12,000 fpm
Saturated steam Main and auxiliary Headers...Auxiliary Steam and exhaust headers are normally sized for 6000 - 15,000 fpm
Superheated steam Large turbine and boiler leads 10,000 - 20,000 fpm

You might check the Piping Handbook (Crocker & King) or Navco Datalog
 