Pavan Kumar
Chemical
- Aug 27, 2019
- 334
Hi All,
We have Tank that is designed to overflow to a small tank that drains to a sewer. The smaller tank is vented to atmosphere. The system sketch is attached with this post. The overflow line is 6" Sch 10. I want to verify if the line is sized correctly. I read through paper by PD Hills " Designing Piping Systems for Gravity Flow". In the flow rate of the overflow is same as inflow rate which is 35 gpm. I calculated the line size as 4" by maintaining JL* to be less than 0.3 for side outlet piping from vessels in PD Hills paper. Also we want to install a 4" ON/OFF valve on the over flow at the bottom end as the overflow line size is required is only 4". he in flow valve will be closed when the 4" ON/OFF valve is closed. I can install a 6" valve too but a 4" would be cheaper and less heavier for installation and maintenance. The intention of installing the ON/OFF valve is have a control the drainage of the waste water until its PH is brought to spec.
1. I want inputs from you all if you the 4" line size for self venting flow is correct or not.
2. I also want to know if by installing the 4" ON/OFF valve am I changing anything. I understand that when the valve opens after a while initially there will be full pipe flow followed by half-pipe flow.
Thanks and Regards,
Pavan Kumar
We have Tank that is designed to overflow to a small tank that drains to a sewer. The smaller tank is vented to atmosphere. The system sketch is attached with this post. The overflow line is 6" Sch 10. I want to verify if the line is sized correctly. I read through paper by PD Hills " Designing Piping Systems for Gravity Flow". In the flow rate of the overflow is same as inflow rate which is 35 gpm. I calculated the line size as 4" by maintaining JL* to be less than 0.3 for side outlet piping from vessels in PD Hills paper. Also we want to install a 4" ON/OFF valve on the over flow at the bottom end as the overflow line size is required is only 4". he in flow valve will be closed when the 4" ON/OFF valve is closed. I can install a 6" valve too but a 4" would be cheaper and less heavier for installation and maintenance. The intention of installing the ON/OFF valve is have a control the drainage of the waste water until its PH is brought to spec.
1. I want inputs from you all if you the 4" line size for self venting flow is correct or not.
2. I also want to know if by installing the 4" ON/OFF valve am I changing anything. I understand that when the valve opens after a while initially there will be full pipe flow followed by half-pipe flow.