electromike
Electrical
- May 22, 2003
- 28
I have encountered a situation with GE motor starters where the OL selection chart for a size 5 starter with CTs and a 168 Fla at 150 hp calls for almost a double size heater element than what would be expected with a 5 amp secondary current on the CT. The heaters recommended by the chart would be for about a 8 to 9 fla. I would expect about a 4 or 5 not 8 or 9. Does anyone have a explanation for this?