cfarmer
Structural
- Oct 17, 2003
- 12
Designing slab on grade to support significant rack loads (15000# per post) and using PCA charts to design it appears as though a plain slab is off the chart (when considering 2 adjacent racks back to back will give 2-15000# post loads only 8" apart). Using finite element analysis software (ROBOT) we have determined the max moment to be 40kN-m. Which lends to a 10" slab with 15M @ 12" o.c. E.W top and bottom or 20M @ 10" o.c. ea. way at centre of slab. This seems like a very significant slab, especially to the ears of the client, but it is what it is!
Does anyone have experience with this type of design with respect to this reinf. and thickness?
Secondly, if I go with 20M @ 10" oc. I will sawcut at about 12'-6" o.c. ea way across the slab, but if we elect to use 15M top and bottom, can I elminate the sawcutting all together? (can't sawcut with only 2" cover). Any experience on what option would be best with respect to cost and performanc?
Thanks in advance for any thoughts.
Does anyone have experience with this type of design with respect to this reinf. and thickness?
Secondly, if I go with 20M @ 10" oc. I will sawcut at about 12'-6" o.c. ea way across the slab, but if we elect to use 15M top and bottom, can I elminate the sawcutting all together? (can't sawcut with only 2" cover). Any experience on what option would be best with respect to cost and performanc?
Thanks in advance for any thoughts.