jochav52802
Structural
- Nov 28, 2018
- 81
Good Day!
I'd appreciate some help with the following topic.
I've got an existing 6" slab that needs to support some new large concentrated moments and vertical loads. Unfortunately, the slab is not thick enough to provide adequate post-installed anchor embedment to resist the loads. As a result, I've proposed to demo an area of the slab so that it can be thickened to a depth sufficient to provide enough anchor embedment, while also utilizing dowels to maintain the slab's prior moment capacity/continuity. Please see my attached PDF sketch for my approach.
Questions:
1) Does this approach make sense, and is it aligned with common practice for similar situations?
2) After the existing slab area is demoed, will specifying the remaining perimeter area of concrete to be roughened to 1/4" amplitude be enough to re-engage the one-way & two-way shear capacity of the slab, or will the new interface create a weak-spot that I won't be able to overcome?
As a side note, if you're wondering why my sketch is showing hairpins/anchor reinforcement, our loads were so high that Section R17.2 of ACI 318-14's requirement to provide a rigid base plate was leading to an unreasonably thick base plate. As a result, we chose to bypass that requirement by providing anchor reinforcement/hairpins, in order to eliminate the brittle concrete breakout cone load path and replace it with a ductile anchor reinforcement load path, (we sized the base plate sufficiently to keep it's stress below allowable.) I confirmed with ACI's technical support that this is in line with the intent of Section R17.2 of ACI 318-14. A downside of eliminating the need for a rigid base plate is that I now need a thicker replacement section in order to make room for the anchor reinforcement's development length on each side of the anchor breakout cone.
I appreciate your time and comments!
I'd appreciate some help with the following topic.
I've got an existing 6" slab that needs to support some new large concentrated moments and vertical loads. Unfortunately, the slab is not thick enough to provide adequate post-installed anchor embedment to resist the loads. As a result, I've proposed to demo an area of the slab so that it can be thickened to a depth sufficient to provide enough anchor embedment, while also utilizing dowels to maintain the slab's prior moment capacity/continuity. Please see my attached PDF sketch for my approach.
Questions:
1) Does this approach make sense, and is it aligned with common practice for similar situations?
2) After the existing slab area is demoed, will specifying the remaining perimeter area of concrete to be roughened to 1/4" amplitude be enough to re-engage the one-way & two-way shear capacity of the slab, or will the new interface create a weak-spot that I won't be able to overcome?
As a side note, if you're wondering why my sketch is showing hairpins/anchor reinforcement, our loads were so high that Section R17.2 of ACI 318-14's requirement to provide a rigid base plate was leading to an unreasonably thick base plate. As a result, we chose to bypass that requirement by providing anchor reinforcement/hairpins, in order to eliminate the brittle concrete breakout cone load path and replace it with a ductile anchor reinforcement load path, (we sized the base plate sufficiently to keep it's stress below allowable.) I confirmed with ACI's technical support that this is in line with the intent of Section R17.2 of ACI 318-14. A downside of eliminating the need for a rigid base plate is that I now need a thicker replacement section in order to make room for the anchor reinforcement's development length on each side of the anchor breakout cone.
I appreciate your time and comments!