What has primarily been discussed is co-current flow, both steam and condensate flow in the same direction.
What guidelines are used for counter-current steam/condensate flow?
This is a very interesting topic to me. The steam/condensate flow being discussed is two-phase flow (fluid/vapor), mostly vapor, with very little fluid (the intended condition during operation).
The guidelines Mr. Kirsner stated are typical for our designs, and the greater slope recommended by AJN can't hurt if installation costs aren't significantly hurt.
The guidelines seem appropriate to me, provided: the steam quality is high, piping is well insulated, piping is well maintained, system is thoughtfully operated, and if steam velocities are not too high. To the extent these parameters are not controlled or controllable, the design decisions for the line size, slope, and dripleg spacing may need to change. For two-phase flow, as the proportion of fluid increases for a given relatively high velocity, or as the vapor velocity increases for a relatively high proportion of fluid depth, the flow changes from stratified smooth, to stratified wavy, and then slug flow. If that happens the result will probably be water hammer, and in the case of stagnant sub-cooled condensate the result can be condensate-induced water hammer.