If you are outside the building, the plumbing code does not apply. The IPC only applies for plumbing in the building. An 8" sanitary sewer pipe for outside sewer service is generally run at 0.4%. This will yield a velocity of over 2 ft per second when running full, which is the criteria in the Ten States Standards. Ten States has been adopted in almost all of the US for exterior sewer lines. You really should have a civil engineer look at this, as the regulations for sewers outside the building is different from inside the building.
I respectfully disagree with cvg, who is very knowledgeable, concerning his posts above on 27/08/10 1:04 and 12:09. Ten States clearly states that the minimum sewer velocity (slope) is based on the pipe flowing full. A 1% slope on an 8" pipe is not required by code, at least according to Ten States, which has been adopted by Florida and Georgia in which I practice and I believe by at leat 40 other states. Obviously there are situations in which the standard minimum regulations should be exceeded, but I don't see anything special in this situation as described.