Going back to this thread and I had an issue on site with the Contractor, Concrete Testing Agent, and Concrete Supplier/QC person while on site.
Our specification states we need a MINIMUM of (1) test for slump and air content per ASTM guidelines which state to perform these test in the middle third of the pour. Usually this isn't a problem at job sites because they test prior to the pour for acceptance and then test again during the middle third for our records. Results usually stay the same or don't vary by a large magnitude.
I was met with a lot of push back from the contractor, testing agent, and supplier for this particular job. All of them said it was strict and never have seen it tested in the middle in their 20-30 years of experience. They refused to test the first truck at the middle and all hell broke loose. Their reasoning was that they had a previous job in which the concrete had to be replaced. I'm the EOR as well and had to call the contractors supervisor to get the subsequent trucks tested in the middle.
Our specification requires air content to be 6% plus or minus 1%. The second and third trucks met spec prior to pour but the air dropped to 3.5% when tested at the middle third. What course of action should I take or taken in the field? Is our specification too strict? What is y'alls experience with the ASTM guidelines versus acceptance?
Going back to this thread and I had an issue on site with the Contractor, Concrete Testing Agent, and Concrete Supplier/QC person while on site.
Our specification states we need a MINIMUM of (1) test for slump and air content per ASTM guidelines which state to perform these test in the middle third of the pour. Usually this isn't a problem at job sites because they test prior to the pour for acceptance and then test again during the middle third for our records. Results usually stay the same or don't vary by a large magnitude.
I was met with a lot of push back from the contractor, testing agent, and supplier for this particular job. All of them said it was strict and never have seen it tested in the middle in their 20-30 years of experience. They refused to test the first truck at the middle and all hell broke loose. Their reasoning was that they had a previous job in which the concrete had to be replaced. I'm the EOR as well and had to call the contractors supervisor to get the subsequent trucks tested in the middle.
Our specification requires air content to be 6% plus or minus 1%. The second and third trucks met spec prior to pour but the air dropped to 3.5% when tested at the middle third. What course of action should I take or taken in the field? Is our specification too strict? What is y'alls experience with the ASTM guidelines versus acceptance?