I was hoping I could get some help on this subject.
I am designing a new 480V high impedance, 2500kVA generator paralleling generator system that connects 2 generators to a 12kV bus via seperate 2500kVA Delta/wye-low impedance grounded transformers. The 12kV system feeds 10-1000kVA D-Y transformers.
I am concerned about transformer inrush. I have requested the nameplate information for each transformer - assuming 12x for now.
My approach.
I figured out how much current the generators can put out from the x''d (.1 pu) which is roughly 30kA per generator. I am assuming the transformers will not be energized until both generators are connected to the bus at full voltage. I added the GSU xfmr and reflected the generators on the 12kV side and the available current after the GSU transformer is 750A for a total of 1500A.
I know that the transformers will want 577A (12kV) of inrush current (assuming 12x fla - waiting on info) 1000kVA/(12kV*1.73) * 12 =577A per xfmr * 10 = 5773A for all 10 transformers.
I know the transformers will still get energized even though they don't get teh full current, but will take additional time.
I am kinda stuck here...I am pretty sure the generators control system, excitation will play a huge role in this model, also the 480V gen braker, generator thermal damage curve, MV SEL-751A relays will also have to be programmed to accomadate the inrush currents.
Any additional documents, rules of thumbs, etc... would be greatly appreciated. I am working on getting ATP to try and build this model, but any other insights would be great.
I am designing a new 480V high impedance, 2500kVA generator paralleling generator system that connects 2 generators to a 12kV bus via seperate 2500kVA Delta/wye-low impedance grounded transformers. The 12kV system feeds 10-1000kVA D-Y transformers.
I am concerned about transformer inrush. I have requested the nameplate information for each transformer - assuming 12x for now.
My approach.
I figured out how much current the generators can put out from the x''d (.1 pu) which is roughly 30kA per generator. I am assuming the transformers will not be energized until both generators are connected to the bus at full voltage. I added the GSU xfmr and reflected the generators on the 12kV side and the available current after the GSU transformer is 750A for a total of 1500A.
I know that the transformers will want 577A (12kV) of inrush current (assuming 12x fla - waiting on info) 1000kVA/(12kV*1.73) * 12 =577A per xfmr * 10 = 5773A for all 10 transformers.
I know the transformers will still get energized even though they don't get teh full current, but will take additional time.
I am kinda stuck here...I am pretty sure the generators control system, excitation will play a huge role in this model, also the 480V gen braker, generator thermal damage curve, MV SEL-751A relays will also have to be programmed to accomadate the inrush currents.
Any additional documents, rules of thumbs, etc... would be greatly appreciated. I am working on getting ATP to try and build this model, but any other insights would be great.