JCianfarra
Mechanical
- Jul 10, 2012
- 15
I came across a light hazard occupancy room with two standard doors and a dimension of 18'2 x 30'3 (~550sf < 800sf) so I determine it meets the defenition of a "Small Room". If I spaced my sprinklers along the room width 4'1 _ 10' _ 4'1 and 7' _ 14'3 _ 9' along the room length, both my average sprinkler and individual sprinklers areas are less than 225sf. However the length of the room being over 30' is making me second guess myself. The appendix section of NFPA-13 shows a room length of 30' in the example, but it does not indicate this is a maximum length. Based on the 26'8 width of the room in the Appendix example (d), if the length were any longer the average sprinkler areas would be exceeded. But, this is not the case in my example since the room is only 18'2 wide. Simply asked "Is the 30'3 room dimension too long?" I uploaded a pdf of the image to make it more clear. Thanks!!