Smoke detector for high ceilings

Status
Not open for further replies.

katwalatapan

Electrical
Aug 9, 2011
153
Hello,

I have a query concerning installation of a smoke detector in area of 16' high ceilings. Would the same installation requirements be applicable as for regular 7' ceilings or are they required / preferred to be wall mount at lower heights to allow for accurate smoke detection?

Thank you.
 
Replies continue below

Recommended for you

You may want to red-flag this posting and repost in forum184

TTFN
faq731-376
7ofakss

Need help writing a question or understanding a reply? forum1529


Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com:
 
Smoke rises, hot air rises.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
katwalatapan,
I think the best thing to do is ask AHJ.
NFPA 72-2016 (alarm systems) is now out and for sale. I heard that supposedly a lot of major changes from 2013.
Good luck,
Dave
 
If you put them on the wall at 7 feet, they _might_ go off before the flashover.



Mike Halloran
Pembroke Pines, FL, USA
 