Vusal Quliyev
Mechanical
- Dec 4, 2018
- 26
Dear Friend,
I received one high rise Residence project to check. There is stairway pressurization system and corridor exhaust system applied by designer. There is lift lobby located between corridor and stairway. No any pressurization considered at lobby.
Building consist of 33 level and height is 133 m.
Designer considered total 10900 l/s stairway pressurization (325 l/s for each).
There is only 200 l/s exhaust rate considered for smoke exhaust which is located at corridor (Shaft size is only 200x300 mm for smoke exhaust).
Please find attached schematic drawing and floor plan for you consideration.
I am confused. What do you think about this situation?
Additional information
Building totally protected by sprinkler.
There is no any rational analysis concluding how these values were derived. Minimum and Maximum differential pressure at doors are: 15 Pa and 65 Pa.
I received one high rise Residence project to check. There is stairway pressurization system and corridor exhaust system applied by designer. There is lift lobby located between corridor and stairway. No any pressurization considered at lobby.
Building consist of 33 level and height is 133 m.
Designer considered total 10900 l/s stairway pressurization (325 l/s for each).
There is only 200 l/s exhaust rate considered for smoke exhaust which is located at corridor (Shaft size is only 200x300 mm for smoke exhaust).
Please find attached schematic drawing and floor plan for you consideration.
I am confused. What do you think about this situation?
Additional information
Building totally protected by sprinkler.
There is no any rational analysis concluding how these values were derived. Minimum and Maximum differential pressure at doors are: 15 Pa and 65 Pa.