Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Snow Drift from Gable Roof onto Deck

Status
Not open for further replies.

TAB_HOO

Structural
Sep 2, 2022
6
I have a 4 on 12 gable roof sloped down to a 12' wide deck below. How should I figure out my snow drift? Particularly my upper roof fetch length? Is it the full width of the roof, eave to eave, or just the distance from the eave to the ridge? All of the examples I've seen are flat roofs with different levels.
 
Replies continue below

Recommended for you

You have drift load and sliding snow load. Values should be in the code.

BA
 
TAB_HOO

Where is the building located? What is the appropriate building code for that location?


Jim

 
For the length of the roof upwind of the drift, lu, you can conservatively use the distance of the entire roof from eave to eave. The distance from ridge to eave would be unconservative since some snow will definitely make it over the ridge and contribute to your drift load.

It may also be a appropriate to use lu = 0.75*La + Lb (see the image below) due to some of the snow getting trapped on the leeward side of the roof. The commentary (C7.7 of ASCE 7-16) suggests using a procedure like this for stepped roofs. There is also an example in the "Guide to the Snow Load Provisions of ASCE 7-16" that is exactly like your question where they apply the same 0.75 factor to the windward side of a gabled roof in their snow drift calculation.

Snow_Drift_Dimensions_of_Gable_Roof_wck197.png


Structural Engineering Software: Structural Engineering Videos:
 
Thanks for the replies!

jimstructures: The building is a house in Bedford, Virginia. The appropriate code is the 2018 Virginia Residential Code (2018 International Residential Code with Virginia Amendments). Ground snow is 25 psf.

ProgrammingPE: I thought the eave to ridge distance would be unconservative for my upper roof fetch length (lu), but I also thought some of the snow might get trapped on the roof. The example you referenced in "Guide to the Snow Load Provisions of ASCE 7-16" is "FAQ 10", correct?

 
I love the response from ProgrammingPE, something I will think about a bit more. Up to this point in time, I've concluded that I would use the entire length of the roof unless the roof pitch was greater than 7:12, similar to the point when unbalanced snow loads need not be considered. Once it exceeds 7:12, I've concluded that if ASCE isn't worried about snow load blowing from one side to the other then we wouldn't need to include the full length of the roof for lower drift.
 
Yes, "FAQ 10" in "Guide to the Snow Load Provisions of ASCE 7-16" appears to be identical to what you are describing.
 