sawoods
Structural
- Aug 13, 2012
- 4
I am currently evaluating an existing building structure. There is a small office space, about 30'x70'x12' tall, tacked onto the front of a warehouse space that is 25' high and a roof length of 550' that is dumping snow drift on the office roof. The ground snow load is 20 psf (Ohio). The building, both office and warehouse, were built in 1971. The drawings say the building was designed for 25 psf live load. In evaluating the office roof joists for their ability to carry the drift load, they fail spectacularly, just like seemingly every existing building I run into. We are working for the contractor on this job, who is working for the building owner. I informed the contractor about the structural issue, and that additional joists should be installed. Of course the contractor doesn't want to spend more money, so his answer was that as long as the building met the building code when it was built, and we don't add any load to it, we don't have to reinforce the roof. So my questions are: Why do all the existing buildings I evaluate always fail to carry the snow drifts (according to the calcuations, they work in real life)? Did old building codes not include snow drifts? If so, when did snow drifts become part of the code? Apparently Ohio didn't adopt a national code until the late 70's, and I can't find a copy of the Ohio Building Code from 1971 to see if it included drifts.