Soft Starter for High Inertia Fan Motor Single Phase 5 HP 2

Status
Not open for further replies.

JohnMcNutt

Industrial
Mar 3, 2013
111
Been looking around for a product that meets specification to soft start a single phase fan motor.

5 HP, 3500 RPM, 230 V, 21A nominal, 60 Hz. Currently started DOL but would like to limit inrush to make it easier on standby generator. Current acceleration time is 2-3 seconds estimated.

This product from Carlo Gavazzi looks promising:

However, on page 10 they seem to limit it to a 3 HP application.

Do you know of an alternate product that would meet specifications?
 
Replies continue below

Recommended for you

Forget it. Not gonna happen.

You want to cut the generator some slack? Get a VFD that can dish out 3ph while taking in 1ph. Replace the overwrought 1ph 5hp with a used 5hp 3ph. It will last longer, run cooler, can be speed adjusted, and the VFD can provide sublime soft starting.

Keith Cress
kcress -
 
What he said.

I have used such 'soft starters' for high speed 3 phase blower motors in our shop and the inrush current has always been high regardless of the voltage levels. At those low HP levels, the cost difference between a soft starter and VFD can't be too high. VFD also gives the big advantage of speed control and hence flow control of the fan, if needed.

Muthu
 
21A nominal
What is "Nominal" current"?
Use nameplate rated current.
My tables indicate a typical full load current for a 230 Volt 5 HP motor as 28 Amps.
A rule of thumb that has never let me down for motor starting DOL; The generator capacity must be equal to or greater than the existing load plus three times the rated current of the motor being started.
There may be a noticeable but generally acceptable voltage dip when the motor starts.
But, determine the nameplate rated current and if it is less than 25 Amps, then contact the manufacturer of the device for information.
Note: Standby generators and soft starts don't always work and play well together, especially if the soft start is a major load on the generator..

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Others have covered the motor side but if you're going to spend any money, there are upgrades you can make on the generator end as well. You haven't specified what your kW is but regardless, a better voltage regulator or even better, permanent magnet based excitation do wonders to keep voltage stable during big motor starts.
 
Soft starters for single phase motors are problematic depending on the TYPE of single phase motor. Capacitor Start motors do not fare well with soft starters and neither do the soft starters fare will with them; it’s usually a race to see which one fails first. The same is true for VFDs on single phase motors. You can use Soft Starters (and VFDs) on PSC type (Permanent Split Capacitor) single phase motors, but the likelihood that your 5HP motor is PSC is low.

Before wasting money on questionable electronics, make sure that your bower has a damper and that the damper is CLOSED when starting. It seems counter intuitive to many people so they open or remove the dampers. What that does is to immediately put load on the motor, making it take longer to accelerate. If there is an open damper, close it and try it again.



" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
If the motor is too large for the generator to start comfortably, a stable voltage may make things worse.
The overload slows the generator down.
When the generator slows down, the frequency drops.
With a stable voltage and a falling frequency the motor may saturate magnetically.
The current may be excessive and that will make matters worse.
All quality AVRs have a feature called Under-Frequency-Roll-Off. (UFRO)
When the frequency drops more than about 3 Hz, the AVR reduces the voltage in proportion to the frequency drop.
It is generally not possible to easily add a Permanent Magnet Generator (PMG)to an existing machine.
PMG helps with short circuit tripping.
For motor starting, a PMG may be overruled by UFRO.
If you are buying a new generator by all means specify a PMG if it is available.


Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
It may be necessary to start large motor before the smaller motors.
It may be necessary to shed load before starting a large motor.
It may be necessary to buy a larger generator.
Without seeing your complete setup, it is difficult (impossible) to give much help.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
5hp is too large for residential and in range for commercial and industrial. I'd be surprised if the standby generator is less than 50kW but OP needs to fill us in on this detail.

Waross, I have an interesting situation that occured before I started at the company. They got water in a 50kW alternaror enclosure and blew it up. A 50kW replacement was not available in the timeframe they wanted but a 75kW was available in the frame size so it was purchased. The prime mover was not replaced. They also electrified a mechanical pump with a 25 horsepower electric motor on DOL start. You have to hold the start button down until the motor is up to speed on the 50kW set due to the voltage drop not being able to hold in the contactor. The 75kW set starts it up just fine. On small sets the regulator is powered directly off the windings and any hit that causes a voltage drop also reduces the powered available for excitation which causes double trouble.
 
As it stands, the installation has an old existing 22 kw genset, shunt excited, that will barely start the motor (and I mean just barely) with a maximum of grunting and frequency loss. But it comes up to speed, eventually. (The fan was installed with no consideration for this).

The owners are proposing a 30 kw genset, shelf model because of time constraints and market availability problems due to current events. Auxiliary winding excitation power. UFRO is standard equipment. Stated motor starting of this model is 44 kW, and this is a code J motor, 7.99 multiplier * 5 HP = 40 kW demand to start at 35% voltage dip.

The only other significant loads here are two AHU air conditioners (2-3 tons each) plus plugs and lights for maybe a thousand square feet of offices.

Our thinking at this point would be that automatic shedding (total load current, frequency, and voltage sensing) to drop the AC units if necessary should be adequate, since plugs and lights will be well below the 4 kw surplus we show available here.

Since the original post, I have discovered Baldor offers a soft start for motors of this size (and larger), but based on advice here, that seems like a bad solution.

It may be slicing it thin to use all 44 kw of motor starting capability, 40 for motor start and 4 for house loads, but it does seem to fit into the specs (barely). And since it already starts with an existing old and decrepit genset, it should work. In an ideal world we would go larger, but they want it to be in service sooner than later.

Thoughts?
 
When you spec a higher KVA generator just for starting the motor DOL, isn't that an inefficient use of the DG with attendant low load wet stacking of the engine and additional fuel consumption and maintenance costs?

Muthu
 
I am still interested in expanding on the initial comments on this thread.

We have also discovered Stellar makes a whole range of them for the application, but have no experience with the company.

They specifically list CS/CR 1ph 230V motors as the application for these starters.

What about them does not play well together? Are the soft start manufacturers making junk that will be problematic in the long run?
 
When you spec a higher KVA generator just for starting the motor DOL, isn't that an inefficient use of the DG with attendant low load wet stacking of the engine and additional fuel consumption and maintenance costs?
I have had this discussion before.
Life is hard for a standby generator.
From a cold start, within a few seconds they may be hit with a significant overload.
Then they may run at a low load level.
If you have to start the motor, you have to do what you have to do.
My worst case was a plant serviced by a 275 KVA set that normally ran at about 10% load.
The plant used one large motor for a few hours a day.
The set worked hard for a few seconds starting the large motor and then the load dropped to about 25%.
Once started, the large motor was generally lightly loaded.
And yes, wet stacking is an issue that I have encountered several times with standby sets when there is a lot of A/C involved.
I have encountered a couple of new sets that wet stacked badly.
Several days on a load bank was sufficient to seat the rings and avoid further wet stacking.


Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
What about them does not play well together? Are the soft start manufacturers making junk that will be problematic in the long run?
It has to do with the current and voltage wave forms caused by the soft starter chopping the sine wave.
Many AVRs have trouble properly sensing the voltage of the interrupted sine wave.

Our thinking at this point would be that automatic shedding (total load current, frequency, and voltage sensing) to drop the AC units if necessary should be adequate, since plugs and lights will be well below the 4 kw surplus we show available here.
That is a road that I have traveled many times.
I installed a lot of standby sets in the tropics.
Anyone who could afford a standby set generally had a lot of A/C.
A lot of sets were brought in in one order. All were sized by someone else and all were undersized.
My first learning experience:
The power failed and the set started and transferred automatically.
The A/C load caused the voltage to drop so far that the contactor in the ATS opened.
The set recovered speed and voltage.
The ATS reconnected and the A/C load pulled the frequency down again.
This repeated until the repeated arcing in the contactor burned one of the main contacts so badly that it no longer made contact.
Then at least the lights came on. (Half of the lights powered by the remaining contact and the remainder powered in series with the stalled A/C units.
Solution:
Small relays were installed in the A/C control circuits.
A push button would energize the relay and one set of contacts would seal the relay in, a second set would control the A/C.
When the power failed, all of the relays would drop out and the standby set would come on-line with no A/C load.
The owner would then select which individual A/C units to restart, within the capability of the gen-set.

There are also compressor protection relays available.
The three phase models monitor voltage, and phase sequence.
They will not operate if the voltage is too low or too high.
They will not operate if the phase sequence is reversed.
I used one of these and a lot of control relays to protect all of the refrigeration equipment in a sausage factory.
One day the utility changed out the transformers and put 416 Volts into a 208 Volt system.
They lost computers, calculators, lights, fax machines, and copiers.
The protection system saved all of the refrigeration equipment and no product was lost.

The single phase protectors were generally plug-in devices intended for refrigerators, freezers and small A/C units.
They would shut down on over voltage or under voltage. They provided automatic restart after a random time delay on the order of three minutes.
You may roll-your-own with a time delay relay that drops out on a power failure and re-closes after a suitable time delay that allows time for the large motor to start.


Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
In case I have not made this clear. There is no probability of all loads starting at once. The large fan does not start until controls tell it to start, and air conditioners these days all have variable delay built in.

I understand how SCR soft starters chop the waveform. And have some idea on how that can affect AVRs similar to the pulses in a VFD supply, but not a very deep understanding of what might actually happen.

But our experience has been that some more pre-packaged soft starters of a similar concept, though less industrial in nature, have been met with nothing but great success in smaller generators and standard hermetic compressors up to 5 HP. But ramp time is very fast.

Do you feel that the longer ramp time in the heavy fan will mess with the AVR more likely?
 
Something to keep on mind during all of this is that small genders, less than 50kW, are often not rated according to NEMA or IEC guidelines and as a result are difficult to size correctly. Many manufacturers use bogus terms in the rating such as "peak" so it's it's difficult to predict how the generator will actually behave.

If line side harmonics are a problem for the AVR you could always go old school and use a transformer based soft start.
 
Do you mean a "Roll-your-own" auto-transformer start, Tug?
Could work.
A 240:120 Volt transformer with the windings connected in series would develop about 66% voltage on the tap.
For continuous running you would need a 5 KVA transformer.
For starting duty I would go with a 2 KVA or 2.5 KVA transformer.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
I've still got a few magnetic soft starts in my fleet and even a pair of resistor based units.
 
Tugboat

Given that this high inertia fan is struggling even with full voltage (sans the line drop), I don't see how any voltage reduction methods, be it soft starter or auto trafo, helps in getting it up to speed.

Bill

With the increased capex cost, fuel cost, maintenance cost and not to mention diesel tantrums of a higher rated DG, a quality VFD (with an even VFD bypass on full speed) seems to be a no-brainer to me. Motor start and speed control tech has increased manifold from ward leonard system to VFD.

Muthu
 
Auto-transformer starters were the starter of choice for high inertia loads such as fans. And, by the way the inertia of a fan was nothing compared to the inertia of a large chipper wheel.
An auto-transformer start will accelerate a fan quite well with reduced starting current.
If the inertia was too much for an auto-transformer starter the next step was a wound rotor motor. Think a large sawmill band-saw with twin 8 foot diameter band wheels.
The economics of a standby generator which may run a few hours a year have no relationship to the economics of a prime power generator or a grid connection.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 