Can anyone offer suggestions for configuration of an ATS48 softstarter in a 125 hp centrifugal blower application? Specifically, beginning settings for startung torque, current limit and ramp time?
With ramp time of 15 secs, my current limit needs to be as high as 400% to allow motor to get up to speed (otherwise we go out on overload). We are starting with a closed inlet damper on the blower to reduce load.
I thought I might be able to reduce the starting current requiremetn to less than 400%.
Thanks